SENSOR
Bulk Data Entry Sensors may be used to activate loads.
Format
(1) | (2) | (3) | (4) | (5) | (6) | (7) | (8) | (9) | (10) |
---|---|---|---|---|---|---|---|---|---|
SENSOR | SID | TYPE | STYPE | COMP | ID |
Continuation line if TYPE=TEMP
(1) | (2) | (3) | (4) | (5) | (6) | (7) | (8) | (9) | (10) |
---|---|---|---|---|---|---|---|---|---|
LSID | GID | LBOUND/LTID | UBOUND/UTID |
Continuation line if TYPE=DISP,
SPCF, or FORCE
(1) | (2) | (3) | (4) | (5) | (6) | (7) | (8) | (9) | (10) |
---|---|---|---|---|---|---|---|---|---|
COND | CTYPE | LBOUND | UBOUND | ||||||
ACTION | ATYPE |
Example
(1) | (2) | (3) | (4) | (5) | (6) | (7) | (8) | (9) | (10) |
---|---|---|---|---|---|---|---|---|---|
SENSOR | 2 | TEMP | 4 | ||||||
4 | 933 | 100.0 | 200.0 |
Definitions
Field | Contents | SI Unit Example |
---|---|---|
SID | Unique sensor
identification number. No default (Integer > 0) |
|
TYPE | Sensor type. No default |
|
STYPE | Sensor sub-type.
|
|
COMP | Component of the specified
SENSOR type. For TYPE=DISP or SPCF: TX, TY, TZ, RX, RY, RZ, T, or R For TYPE=FORCE: FX, FY, FZ, MX, MY, MZ, F, or M |
|
ID | Entity ID for the
specified SENSOR type. For TYPE=DISP or SPCF: Grid ID. For TYPE=FORCE: Section ID. |
|
Descriptions for TYPE=TEMP: | ||
LSID | Load set identification
number of a QBDY1 or QVOL Bulk Data Entry. No default (Integer > 0) |
|
GID | Grid or scalar point
identification number. No default (Integer > 0) |
|
LBOUND/LTID | Lower bound of the
temperature range, or the table identification number of a
TABLEDi entry which specifies the lower bound
as a function of time. No default (Real or Integer) |
|
UBOUND/UTID | Upper bound of the
temperature range, or the table identification number of a
TABLEDi entry which specifies the upper bound
as a function of time. No default (Real or Integer) |
|
Descriptions for TYPE=DISP, SPCF, and FORCE 3 | ||
COND | Continuation line flag indicating that condition information is to follow. | |
CTYPE | Condition type.
No default |
|
LB, UB | Lower and upper bounds,
which are interpreted based on the defined Condition Type
(CTYPE). No default (Real) |
|
ACTION | Continuation line flag indicating that action type information is to follow. | |
ATYPE | Action type. This
specifies the action performed when the above conditions are satisfied.
|
Comments
- A SENSOR with TYPE=TEMP can only be activated once. Sensor with TYPE=TEMP is supported only for Transient (linear and nonlinear) Heat Transfer analysis.
- The presence of the SENSOR Bulk Data Entry with TYPE=TEMP turns off the referenced LSID loading outside the defined temperature range and turns on the LSID loading inside the temperature range (LBOUND/LTID to UBOUND/UTID).
- SENSORs of TYPE=DISP, SPCF, and FORCE are only supported for Implicit Nonlinear Static and Implicit Nonlinear Transient analyses. Any number of conditions and actions can be specified, and the corresponding conditions and actions are appropriately combined.